Dirt and mould in the outside units such as at the exchanger, valve stuck, icing of the outside exchanger, low gas, faulty thermostat can be most of the major reasons for failure to warm. It would be worth getting the units checked and if needed serviced. Exchanger fans may also be faulty, this will mean inefficient exchange of heat energy.
As most are aware, in heating mode the outside exchanger’s role is to “cool the outside air” (adsorb the heat from the outside air), the inside exchanger releases that heat. As it gets colder outside the exchange becomes less efficient, but at temps even several degrees below zero the exchange should be still very good. In cooling mode the role is reversed, heat is adsorbed by the inside exchanger and heat is released to the outside.
When in heating mode, the outside exchanger should be blowing air colder than the outside air temperature,. While the unit is actively trying to heat inside air to the set temperature the outside fan should be blowing a reasonable amount of volume of cold air, as it gets closer to the desired temperature inside, the volume of air movement outside should reduce considerably.
Most units are designed to work even at temperatures of around -15 C. Most refrigerants used in domestic units such as R-32 have very low boiling points (temps below -30 odd C (R-32 is around -52 C). So at -15 C there is enough difference that a unit should still heat well. Daikin manufacture R-32 and use R-32 as the refrigerant in their units.
Daikin rate their units to work at the following temps
| Outdoor Operating Range | Cool (°CDB) | -10 to 46 |
|---|---|---|
| Heat (°CWB) | -15 to 18 |
Heat pump hot water systems rely on this same heat exchange system to heat the water in the tank by adsorbing heat from the outside air (they try to cool the outside air
). They release the adsorbed energy into the water causing it to get hot. The house is no different to this process.